Spurious RCD trip due to capacitance

Hi All


I've been asked a question re RCD trip, as follows:  

The issue is that in some cases where we have really long runs of cables the capacitive current is calculated to be greater than 100mA. Therefore setting the earth leakage protection down to 100mA would cause nuisance tripping.


By my calcuation for 60 Hz and 400 V you'd need about 700 nF


Has anyone got any experience of this?
Parents
  • Interesting question, depends on the configuration. 


    In a 3ph SWA cable what is lost to earth (armour) by capacitive leakage on one phase will be sucked up by the other phases so there will not be a nett loss to earth, similarly between phases, the capacitive effects will be localised.