Maximum current for a unit supplied from a 13A socket, taking supply voltages into account.

I am currently developing a heated food merchandising unit to be supplied from a 13A three pin plug.


If the unit is designed around 230V, 13A,  do I have an issue when the supply voltage is at the top of its tolerance (230V + 10% = 257V).

As I have a purely resistive load, the current drawn would be 14.3A

Is this an accepted method or should the unit be designed around 257V 13A?


Your help would be appreciated.


Tony Hoare
Parents
  • Is the system expected to draw full current continuously or will the current drop once the system has heated up?  3kw is the normally accepted maximum continuous load for a 13A socket and even at this level low quality plugs and sockets tend to overheat.


    Best regards


    Roger
Reply
  • Is the system expected to draw full current continuously or will the current drop once the system has heated up?  3kw is the normally accepted maximum continuous load for a 13A socket and even at this level low quality plugs and sockets tend to overheat.


    Best regards


    Roger