Maximum current for a unit supplied from a 13A socket, taking supply voltages into account.

I am currently developing a heated food merchandising unit to be supplied from a 13A three pin plug.


If the unit is designed around 230V, 13A,  do I have an issue when the supply voltage is at the top of its tolerance (230V + 10% = 257V).

As I have a purely resistive load, the current drawn would be 14.3A

Is this an accepted method or should the unit be designed around 257V 13A?


Your help would be appreciated.


Tony Hoare
Parents
  • I would recomend that you should design not to exceed 13A at maximum voltage. A few minutes of overcurrent is usually ok, but 45 minutes is around the time constant of typical wiring systems. This unit may be plugged into an already load extension cable and as the attached document shows some of these are not really adequate.


    Best regards


    Roger
Reply
  • I would recomend that you should design not to exceed 13A at maximum voltage. A few minutes of overcurrent is usually ok, but 45 minutes is around the time constant of typical wiring systems. This unit may be plugged into an already load extension cable and as the attached document shows some of these are not really adequate.