This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Loop impedance and RCBO's

Hi Folks,

​For some reason I am unable to access the wiring and regulations forumn, so I have decided to throw this questions to the wolves. I have asked this question to a number of people and continue to get conflicting answers


​Yes or No. Is the circuit below compliant with BS7671 taking into consideration table 41.3 and table 41.5 of BS7671


2.5mm ring circuit approx 60meters long

Earthing arrangment - TNC-S

Ze - Unknown

Circuit Protective Device - BS EN 61009-1  C32A 30mA RCBO 10k

​Measured Zs 1.86ohms

​Max allowable Zs within GN3 0.62ohms

 



Regulation 411.4.9 states that where an RCD has been used to satisfy the requirements of Regulation 411.3.2.2, the maximum values of earth loop impedance (Zs) in Table 41.5 may be applied for non delayed RCDs to BS EN 61009-1




Parents
  • Why is "Ze Unknown" ?? It is recommended to be verified to ensure that there is a suitable supply earth?


    The question is not really whether you can "get away with the high loop impedance" (which you correctly quote the relevant Reg for automatic disconnection for shock purposes if the OPD can't meett 0.4 seconds) but whether what you are looking at is right for the circuit in question.


    Doing some quick calculations myself, and relying on the information you've provided, if the circuit is a ring circuit with total length (of the entire ring) of 60 m, then even with 2.5 T&E, the resistance of the ring R1+R2 at the furthest point should be under 0.3 Ohms at 20 deg C. See Table B1 in GN3, and remember that at the furthest socet on the ring, you're only half way round the 60 m, and then you should, in a healthy ring, have (R1/2) // (R1/2) and (R2/2) // (R2/2).


    So my thinking goes that at least one of the following is likely to be true:


    (i) Ze (or Zdb) is over 1.5 Ohm

            - if it's Ze on a public PME supply, perhaps this is very high (should be < 0.35 Ohm) - it's rather high for TN-S too (0.8 Ohm) ?

            - But if it's Zdb, is the submain OK - what distance and cable size etc.?; or

    (ii) there is at least one fault on the ring circuit; or

    (iii) there is for some reason an issue with the way the loop impedance is being measured - or perhaps a faulty socket outlet / socket outlet switch if low-current loop testing is being used - although this should have shown up in the Ring Final Continuity Tests especially if a socket outlet adaptor were being used?


    Did your Ring FInal Continuity Tests give expected readings for a 60 m ring, for end-to-end R1, R2, Rn, and the cross-checks, before loop impedance testing?


    Of course, there's still the question of L-N fault protection if Zdb is high - what does Ipsc measure at the furthest point on the ring - based on the Zs reading you gave, it could well be 130-180 A? Does that stack up against the Adiabatic Criterion? Looking at Fig 3A5 in BS 7671, the C32 may take up to 20 seconds to operate at that current ... and perhaps the adiabatic criterion cannot be met for 2.5 sq mm?



    Would be interested to know, how do the above thoughts stack up with what you're seeing on-site?
Reply
  • Why is "Ze Unknown" ?? It is recommended to be verified to ensure that there is a suitable supply earth?


    The question is not really whether you can "get away with the high loop impedance" (which you correctly quote the relevant Reg for automatic disconnection for shock purposes if the OPD can't meett 0.4 seconds) but whether what you are looking at is right for the circuit in question.


    Doing some quick calculations myself, and relying on the information you've provided, if the circuit is a ring circuit with total length (of the entire ring) of 60 m, then even with 2.5 T&E, the resistance of the ring R1+R2 at the furthest point should be under 0.3 Ohms at 20 deg C. See Table B1 in GN3, and remember that at the furthest socet on the ring, you're only half way round the 60 m, and then you should, in a healthy ring, have (R1/2) // (R1/2) and (R2/2) // (R2/2).


    So my thinking goes that at least one of the following is likely to be true:


    (i) Ze (or Zdb) is over 1.5 Ohm

            - if it's Ze on a public PME supply, perhaps this is very high (should be < 0.35 Ohm) - it's rather high for TN-S too (0.8 Ohm) ?

            - But if it's Zdb, is the submain OK - what distance and cable size etc.?; or

    (ii) there is at least one fault on the ring circuit; or

    (iii) there is for some reason an issue with the way the loop impedance is being measured - or perhaps a faulty socket outlet / socket outlet switch if low-current loop testing is being used - although this should have shown up in the Ring Final Continuity Tests especially if a socket outlet adaptor were being used?


    Did your Ring FInal Continuity Tests give expected readings for a 60 m ring, for end-to-end R1, R2, Rn, and the cross-checks, before loop impedance testing?


    Of course, there's still the question of L-N fault protection if Zdb is high - what does Ipsc measure at the furthest point on the ring - based on the Zs reading you gave, it could well be 130-180 A? Does that stack up against the Adiabatic Criterion? Looking at Fig 3A5 in BS 7671, the C32 may take up to 20 seconds to operate at that current ... and perhaps the adiabatic criterion cannot be met for 2.5 sq mm?



    Would be interested to know, how do the above thoughts stack up with what you're seeing on-site?
Children
No Data