Loop impedance and RCBO's

Hi Folks,

​For some reason I am unable to access the wiring and regulations forumn, so I have decided to throw this questions to the wolves. I have asked this question to a number of people and continue to get conflicting answers


​Yes or No. Is the circuit below compliant with BS7671 taking into consideration table 41.3 and table 41.5 of BS7671


2.5mm ring circuit approx 60meters long

Earthing arrangment - TNC-S

Ze - Unknown

Circuit Protective Device - BS EN 61009-1  C32A 30mA RCBO 10k

​Measured Zs 1.86ohms

​Max allowable Zs within GN3 0.62ohms

 



Regulation 411.4.9 states that where an RCD has been used to satisfy the requirements of Regulation 411.3.2.2, the maximum values of earth loop impedance (Zs) in Table 41.5 may be applied for non delayed RCDs to BS EN 61009-1




Parents
  • False alarm. Uncalibrated meter! Retesting at the minute and everything is fine
Reply
  • False alarm. Uncalibrated meter! Retesting at the minute and everything is fine