Anomaly between BS62061 and 61508

I am designing a control system for a very big heavy door which has the capability to crush a person and potentially to death although extremely unlikely.  In determining the SIL requirement for the system using BS61508-5 I get the following:



 



Looking at Table E.1 I can derive a qualitative assessment



 



Consequence – Serious permanent injury to one or more persons; death to one person – C2



Frequency of exposure – Rare to more often exposure in the hazard zone – F1



Probability of avoiding the hazard – Possible under certain conditions – P1



Probability of the unwanted event – A slight probability – W2



 



Looking at Figure E.2 this equates to ‘a’ = “No special safety requirements”



 



However if I use BS62061 looking at table A.1 I find “Irreversible: death, losing an eye or arm” Severity Se = 4, then I go to Table A.6 and irrespective of any other criteria it demands a minimum of SIL2.



 



The question is why is there such disparity?  And which is correct?



Thank you,



Rob


Parents
  • Robert,



    I agree with Paul and I would think 62061 would be the correct B standard to apply (or possbibly 13849) as this application is 'high demand'. Once you determined your PL or SIL level you could use a dedicated 'hold to run' safety relay or a small safety PLC if the application is more complex. 



    Andrew
Reply
  • Robert,



    I agree with Paul and I would think 62061 would be the correct B standard to apply (or possbibly 13849) as this application is 'high demand'. Once you determined your PL or SIL level you could use a dedicated 'hold to run' safety relay or a small safety PLC if the application is more complex. 



    Andrew