Exposed-conductive-parts shall be connected to a protective conductor under the specific conditions for each type
of system earthing as specified in Regulations 411.4 to 6.
Simultaneously accessible exposed-conductive-parts shall be connected to the same earthing system individually, in
groups or collectively.
Conductors for protective earthing shall comply with Chapter 54.
A circuit protective conductor shall be run to and terminated at each point in wiring and at each accessory except a
lampholder having no exposed-conductive-parts and suspended from such a point.
and
Regulation 542.1.3.3 [Installation earthing arrangements]
Where a number of installations have separate earthing arrangements, any protective conductors
common to any of these installations shall either be capable of carrying the maximum fault current likely to flow
through them or be earthed within one installation only and insulated from the earthing arrangements of any other
installation. In the latter circumstances, if the protective conductor forms part of a cable, the protective conductor
shall be earthed only in the installation containing the associated protective device.
Have you explored other options, such as converting both installations to TT and using a common earthing system? Although of course, this might not be cheap as additional protective devices and main switchgear assembly equipment, may be required.
Exposed-conductive-parts shall be connected to a protective conductor under the specific conditions for each type
of system earthing as specified in Regulations 411.4 to 6.
Simultaneously accessible exposed-conductive-parts shall be connected to the same earthing system individually, in
groups or collectively.
Conductors for protective earthing shall comply with Chapter 54.
A circuit protective conductor shall be run to and terminated at each point in wiring and at each accessory except a
lampholder having no exposed-conductive-parts and suspended from such a point.
and
Regulation 542.1.3.3 [Installation earthing arrangements]
Where a number of installations have separate earthing arrangements, any protective conductors
common to any of these installations shall either be capable of carrying the maximum fault current likely to flow
through them or be earthed within one installation only and insulated from the earthing arrangements of any other
installation. In the latter circumstances, if the protective conductor forms part of a cable, the protective conductor
shall be earthed only in the installation containing the associated protective device.
Have you explored other options, such as converting both installations to TT and using a common earthing system? Although of course, this might not be cheap as additional protective devices and main switchgear assembly equipment, may be required.