Earthing for Delta connected networks

The generally accepted practice for earthing a network fed from a transformer Delta connection is to use a zig-zag transformer. This will provide a neutral point which can be connected to earth and provide a low impedance path for earth fault currents. I have recently come across some substations in which a Star/Star transformer has been used with the primary star point earthed to provide the earthed neutral point for the MV network. When I look at this arrangement it seems to me that this will provide a high impedance path for earth fault current as there is no flux balance in the core of the earthing transformer. Am I wrong in this assumption? (I would be happy to be wrong on this one). Has anyone come across this arrangement using a Star connected transformer for earthing a Delta system?


thanks

Geoff
Parents
  • HI David,

    Thinking again about the earthing trasformer tank providing the flux path. The flux generated in each limb of the transformer would traverse the oil, essentially a large air gap, this would then be a high reluctance path so I am back to thinking of the star connected earthing transformer providing a high resistance connection to earth.

    regards,

    Geoff
Reply
  • HI David,

    Thinking again about the earthing trasformer tank providing the flux path. The flux generated in each limb of the transformer would traverse the oil, essentially a large air gap, this would then be a high reluctance path so I am back to thinking of the star connected earthing transformer providing a high resistance connection to earth.

    regards,

    Geoff