Isolation requested

Former Community Member
Former Community Member
Good morning All, 


I need to understand something. 

I know the regulation request the isolation as requested for each electrical installations. 

In the scenario where I have the distribution board close to all the electrical equipment (same room)

and each line is separated and protected by their own MCB.

Do I need to install the isolator too? 

I can isolate every circuit directly from the DB?

Thank you and have a nice day
Parents
  • The intention is that you can isolate the whole installation with one switch, rather than having to flip a whole bank of breakers.  If there is a main switch in the distribution board, then that is the isolator.  Otherwise, there should be an isolator before the DB.


    If it's a DB, then that implies that it's just one part of a larger installation.  In which case, is there an isolator at the origin of the supply?