Good morning All, 


I need to understand something. 

I know the regulation request the isolation as requested for each electrical installations. 

In the scenario where I have the distribution board close to all the electrical equipment (same room)

and each line is separated and protected by their own MCB.

Do I need to install the isolator too? 

I can isolate every circuit directly from the DB?

Thank you and have a nice day
Parents
  • Former Community Member
    0 Former Community Member
    If you are looking at a UK installation then the minimum requirement under BS 7671 is covered in regulations group 464, "Switching off for mechanical maintenance".

    461.1 Says that means "shall" be provided, & that it "shall" disconnect all live conductors.

    So, if you are going to remove the local isolator from between the MCB and the heat pump, then for compliance with BS 7671 you will need to isolate at the DB, which must have a 2 (if single phase) or 4 (if 3 phase) pole main switch, as Neutral is a live and current carrying conductor, thus it must also be isolated.


    As a heat pump is also machinery under the Machinery Directive, then a similar requirement is within EN 60204-1, so whichever way you argue the isolator, installation or machinery it is realistically required.

    If the heat pump has a built in isolator then there is the possibility that this can meet the requirements.


    Also the requirement under EN 60204-1 for means of isolation for maintenance is that means of emergency isolation are coloured red/yellow, isolation for maintenance would be coloured black/grey.
Reply
  • Former Community Member
    0 Former Community Member
    If you are looking at a UK installation then the minimum requirement under BS 7671 is covered in regulations group 464, "Switching off for mechanical maintenance".

    461.1 Says that means "shall" be provided, & that it "shall" disconnect all live conductors.

    So, if you are going to remove the local isolator from between the MCB and the heat pump, then for compliance with BS 7671 you will need to isolate at the DB, which must have a 2 (if single phase) or 4 (if 3 phase) pole main switch, as Neutral is a live and current carrying conductor, thus it must also be isolated.


    As a heat pump is also machinery under the Machinery Directive, then a similar requirement is within EN 60204-1, so whichever way you argue the isolator, installation or machinery it is realistically required.

    If the heat pump has a built in isolator then there is the possibility that this can meet the requirements.


    Also the requirement under EN 60204-1 for means of isolation for maintenance is that means of emergency isolation are coloured red/yellow, isolation for maintenance would be coloured black/grey.