RGE trip to full DNO supply

Hi all, Just after peoples thoughts on the following....


We are currently working on a scheme where our client is looking to install 2No. 2MWe RGE to offset the cost of the DNO supply. As part of a study we are conducting we are looking at how the system would react if the 2No. RGE's were to trip and the 4MWe load would be presented onto the DNO network which is already supplying a small portion of the sites demand.  Our aim is to confirm the main HV breakers do not trip or at what load share threshold they don't. 


We are conducting a load flow and fault level analysis using SKM PTW, but this only allows us to look at steady-state scenarios and not a live peak of supply demand. 

My first thoughts are that the HV breakers should be fine as the site will already be up and running i.e. no large motor loads starting or TX inrush, but just want to get other peoples thoughts on how they might approach the subject. 


Thanks
Parents
  • Hi Michael/Geoff, 


    Thanks for taking the time to reply...


    You are correct the REG's will be connected at 11kV level, at this level we have 2No. switchboards and downstream we have 6No. TX which feed the LV systems. We have updated DNO in-feed fault data as they are moving our supply to a better structured side of their network. 


    We will be modelling load flow for approx. 6No. different scenarios and the emergency trip from both RGEs will be among these. 


    Yes we are using SKM and the ISIM may have some value thanks for putting me onto this.
Reply
  • Hi Michael/Geoff, 


    Thanks for taking the time to reply...


    You are correct the REG's will be connected at 11kV level, at this level we have 2No. switchboards and downstream we have 6No. TX which feed the LV systems. We have updated DNO in-feed fault data as they are moving our supply to a better structured side of their network. 


    We will be modelling load flow for approx. 6No. different scenarios and the emergency trip from both RGEs will be among these. 


    Yes we are using SKM and the ISIM may have some value thanks for putting me onto this.