Thermal imaging of cables

Hi all,

So it's a little sunny out, and I have a phone-mounted IR camera, so I thought I'd leave some offcuts of larger cable out to cook in the garden and sense-check my derating assumptions for cables in direct sunlight.


However, I've only really used the IR camera for differential inspections (i.e. that phase is running hotter than the other two) and not worried terribly much about the absolute values, which do change significantly depending on the material emissivity setting.


Can anyone recommend a source for aluminium and copper conductors and black PVC and MDPE / HDPE sheaths after exposure to normal installation treatment? (I.e. sheath roughened a little from pulling in, metal dulled from oxidiation, but neither burnt nor mirror-polished)


The difference between the sunny and shaded side of a 45mm OD single core is quite telling; might try a bundle in trefoil tomorrow!


Jam
Parents
  • Former Community Member
    0 Former Community Member
    Sounds about right - could even be substantially higher.


    Basically, what you are dealing with is difference between what is effectively the air temperature and the sol air temperature along with the resultant temperature rise due to incident radiation.


    If we take a transformer as an example, used somewhere hot and dusty. It's pretty easy to get a unit that can deliver the required power at say an ambient 50C air temperature. You could dump it on a slab and it'll be perfectly happy until the sun comes out - the incident solar radiation will quickly start to raise the temperature of the metal casing to easily 90C or more - it'll take the skin off your hand. If you add a simple shade over the top (usually a dual layer of wriggly tin) then that incident radiation has no effect on the transformer. We tend to use a dual layer at a slope of say 15 degrees as the outer sheet gets red hot, heats the air space between it and the lower sheet by radiation, which induces a convective air current, which keeps the lower sheet much cooler and therefore has much less ability to put incident radiation on the transformer - Happy days, if you need to give that transformer a bit of hard work.


    Ideally, you'd put it inside with mechanical cooling  - but simple shading is quite effective


    Regards


    OMS


Reply
  • Former Community Member
    0 Former Community Member
    Sounds about right - could even be substantially higher.


    Basically, what you are dealing with is difference between what is effectively the air temperature and the sol air temperature along with the resultant temperature rise due to incident radiation.


    If we take a transformer as an example, used somewhere hot and dusty. It's pretty easy to get a unit that can deliver the required power at say an ambient 50C air temperature. You could dump it on a slab and it'll be perfectly happy until the sun comes out - the incident solar radiation will quickly start to raise the temperature of the metal casing to easily 90C or more - it'll take the skin off your hand. If you add a simple shade over the top (usually a dual layer of wriggly tin) then that incident radiation has no effect on the transformer. We tend to use a dual layer at a slope of say 15 degrees as the outer sheet gets red hot, heats the air space between it and the lower sheet by radiation, which induces a convective air current, which keeps the lower sheet much cooler and therefore has much less ability to put incident radiation on the transformer - Happy days, if you need to give that transformer a bit of hard work.


    Ideally, you'd put it inside with mechanical cooling  - but simple shading is quite effective


    Regards


    OMS