530kW motor checks? !!

Former Community Member
Former Community Member
Hello to all, and I do hope that people can advise me on this?


Firstly: what checks can I best do for a possible purchase of a single ABB - AMB 630 LC16 ABA C 530kW pump unit, which is unable to be properly tested (powered up) as the plant it was operating in has been decommissioned, and is currently being scrapped.


The unit appears to be mostly self contained, with a separate 'powercap' capacitor cabinet.

There are 8 in total, in various conditions and all look like this:
200fe3153df9ce950ab8d3220e14538c-huge-1.jpg
b9f52bfa5dd0afd26e92e2d1d4f97d2c-huge-2.jpg
9b08e6def31b626893d8d9e9b05b139f-huge-3.jpg
acf1cd9e473f756f328529e5cb2fc6d0-huge-4.jpg


Secondly: No switching gear is 'included', however I could always ask the company (who's pulling the site apart) if it's possible to obtain the original starter systems maybe???

But would this be a good idea, considering again it's in an unknown condition.


From the 8 available, I've selected 2 that appear to be the most suitable for hopefully reusing again (not bashed about, leaking oil etc) and thus generally look ok, so possibly from that can choose the final one.... but it would be great to know how best to maybe pick the best from any testing that could be done where they stand now, without any power.


Obviously with big industrial machine as this, it's not your average consumer second-hand electrical goods....

....that one just plugs in, and then hopes it works when power is applied!



(Thanks in advance to any replies)
Parents
  • Former Community Member
    0 Former Community Member
    The motor testing on site is probably limited to continuity, winding resistance and ideally a 5kV insulation resistance test.

    However and I apologise if you are familiar with HV working, do not yourself or have anyone working for you access the HV terminals unless you can either see the cables to the motor cut off or the demolition firms authorised person provides a permit in writing. To work on an HV circuit it should first be isolated & earthed and then for your testing the earth removed. Hopefully if the plant was properly shut down ??? the motors will have all been isolated and earthed at the switchboard. I would have expected each motor to have had probablky a vacuum contactor / HV fuse  with an isiolating/earthing arrangement for each motor. The panel then probably fed from a 11kV breaker at one of the power station's substations.

    Some one competent to work on 230/400V low voltage systems would not necessarily be deemed competent to work on HV.

    When doing any tests check out any auxiliary circuits if there are any (i.e. anti-condensation heaters or winding/bearing temperature sensors).

    On a side note in the video a rubber mallet wouldn't cut it to get the end plate off the bearing since it should have a small fit to prevent any chance of ther bearing rotating in the the end plate. Your size of motor will I have a bearing housing which bolts to the end plate and bigger units can have split bearings. Originally there will ahve been clamps to secure the shaft for transport but I doubt you will find them, However as said before protecting the bearings during transport is important (in all 3 planes) other wise the ball/rollers and the races will get damaged. My guess bearing arrangement is ball at NDE and roller at DE. The ball bearing providing the axial location for the motor.

    Not knowing the details of where you want to use the unit, does it have a strong enough supply to support starting this motor? At the power station since supplies will have been probably quite stiff it may have just been DOL or at best Star/Delts unless they used reduced volts etc. to soften the water circuit effects. Just saying make sure your location and local DNO would be OK with this size of motor and possible what kind of starting you will need to consider.


    Hope this helps, good luck.

    Ian
Reply
  • Former Community Member
    0 Former Community Member
    The motor testing on site is probably limited to continuity, winding resistance and ideally a 5kV insulation resistance test.

    However and I apologise if you are familiar with HV working, do not yourself or have anyone working for you access the HV terminals unless you can either see the cables to the motor cut off or the demolition firms authorised person provides a permit in writing. To work on an HV circuit it should first be isolated & earthed and then for your testing the earth removed. Hopefully if the plant was properly shut down ??? the motors will have all been isolated and earthed at the switchboard. I would have expected each motor to have had probablky a vacuum contactor / HV fuse  with an isiolating/earthing arrangement for each motor. The panel then probably fed from a 11kV breaker at one of the power station's substations.

    Some one competent to work on 230/400V low voltage systems would not necessarily be deemed competent to work on HV.

    When doing any tests check out any auxiliary circuits if there are any (i.e. anti-condensation heaters or winding/bearing temperature sensors).

    On a side note in the video a rubber mallet wouldn't cut it to get the end plate off the bearing since it should have a small fit to prevent any chance of ther bearing rotating in the the end plate. Your size of motor will I have a bearing housing which bolts to the end plate and bigger units can have split bearings. Originally there will ahve been clamps to secure the shaft for transport but I doubt you will find them, However as said before protecting the bearings during transport is important (in all 3 planes) other wise the ball/rollers and the races will get damaged. My guess bearing arrangement is ball at NDE and roller at DE. The ball bearing providing the axial location for the motor.

    Not knowing the details of where you want to use the unit, does it have a strong enough supply to support starting this motor? At the power station since supplies will have been probably quite stiff it may have just been DOL or at best Star/Delts unless they used reduced volts etc. to soften the water circuit effects. Just saying make sure your location and local DNO would be OK with this size of motor and possible what kind of starting you will need to consider.


    Hope this helps, good luck.

    Ian