This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Answers Please. Electrical Technology.

1. A load of 2.5kW takes a current of 12 Amp from a 230 Volt supply. Calculate the power factor.


2. Three single phase loads are to be connected to a three phase supply. All at unity power factor. The loads are,


i, 60 Amp.


ii, 50 Amp.


iii, 40 Amp.


By any method determine the neutral current.


Z.
Parents
  • Zoomup:

    1. A load of 2.5kW takes a current of 12 Amp from a 230 Volt supply. Calculate the power factor.


    ANSWER: P.F. = 2500/230 X 12.


                                 = 0.906


    2. Three single phase loads are to be connected to a three phase supply. All at unity power factor. The loads are,


    i, 60 Amp.


    ii, 50 Amp.


    iii, 40 Amp.


    By any method determine the neutral current.


    ANSWER = 16.5 Amps.


    Answers & questions supplied from a City & Guilds and I.E.T. joint publication.


    Z.


     


Reply
  • Zoomup:

    1. A load of 2.5kW takes a current of 12 Amp from a 230 Volt supply. Calculate the power factor.


    ANSWER: P.F. = 2500/230 X 12.


                                 = 0.906


    2. Three single phase loads are to be connected to a three phase supply. All at unity power factor. The loads are,


    i, 60 Amp.


    ii, 50 Amp.


    iii, 40 Amp.


    By any method determine the neutral current.


    ANSWER = 16.5 Amps.


    Answers & questions supplied from a City & Guilds and I.E.T. joint publication.


    Z.


     


Children
No Data