Currently in a dispute with a customer over bootlace ferrules I have used in screw-clamp type terminals - this is an industrial control panel designed to BS EN 60204-1, the wire used is class 5 tri-rated.


The customer says bootlace ferrules are the wrong type and wants them changing to fork-type crimps, arguing that the screw-clamp applies even pressure on fork crimps and a better contact but not so when ferrules are used - if you can picture the bootlace-ferrule on one side of the screw- with its clamp being at an angle as there is nothing on the other side of the screw. However, the termination is tight and makes a good solid contact with the ferrule so I think this is perfectly acceptable.


While I wouldn't generally disagree with a customer, there are hundreds of terminals to change, they didn't specify fork-crimps at design stages and I don't interpret anywhere in BS 60204-1 or BS 60947-1 that ferrules are wrong in screw-clamps.


Any opinions much appreciated.


Parents
  • Former Community Member
    0 Former Community Member
    Sounds like it's just a preference. In these situations I think it's better to turn it round and ask the customer to provide evidence that it's against the standards. You ought to check manufacturers data sheets first but I think it's unlikely that there is a problem.
Reply
  • Former Community Member
    0 Former Community Member
    Sounds like it's just a preference. In these situations I think it's better to turn it round and ask the customer to provide evidence that it's against the standards. You ought to check manufacturers data sheets first but I think it's unlikely that there is a problem.