Is there any issues with applying a Motorised swich disconnector as Incomer instead of MCCB for the auto change over scheme?

Is there any issues with applying a Motorised swich disconnector as Incomer instead of MCCB for the auto change over scheme?

NICK, In order to be safe all switches and/or MCBs must be fully rated to carry the full load current AND be rated to make/break the maximum fault current if a fault develops anywhere down stream.
In your case 400 amps is full load but the fault current could easily be 40,000 amps assuming the incoming transformers/generators each have a 1% impedance when run separately. We normally try to run the 11kV system fault level at under 350 MVA by opening the bus section circuit breaker your auto change-over switch and limit fault current to 25kA.
NICK, In order to be safe all switches and/or MCBs must be fully rated to carry the full load current AND be rated to make/break the maximum fault current if a fault develops anywhere down stream.
In your case 400 amps is full load but the fault current could easily be 40,000 amps assuming the incoming transformers/generators each have a 1% impedance when run separately. We normally try to run the 11kV system fault level at under 350 MVA by opening the bus section circuit breaker your auto change-over switch and limit fault current to 25kA.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site