Diverted Neutral Current

So for the past 5 years if so I have been seeing and experienced a phenomena known as diverted neutral current or diverted networks current.

It has a few names. Much like the incredibly slow realisation that type AC RCDs have had their day. Even though type A has been about over twenty years.

I get at least two / three messages a week from electricians who are now using clamp meters to check the earth conductors of LV installations. Low and behold they find anything from 2A up to 169A in a few cases.

I have research this at work for the last few years and some of the work I have ensured is published via the following link.

http://tangle-tamers.com/page21.html

We have also managed to produce a visual guide for measuring this issue. This work also helped with the Broken PEN IET article. 

It appears the aged life expired state of the LV network is a bigger problem and will only continue to grow. The use of CNE cable has been a tad o IMO. Years ago the RECs admitted cost was the key factor, but made the decision based upon a REC. a government owned network. Since privatisation the DNOs have fixed on fail, leaving the LV side unmonitored to a large extent. This is now slowly changing. But we assume a broken PEN conductor or failure of this can cause hazardous over voltages but also large amounts of network currents bypassing the broken PEN and importing and exporting on domestic earthing in some cases.

whilst the number are small in the scheme or things. It’s a growing issue. The network know about it. But the industry appears to not be discussing it. Why do we not get a safety alert for all electricians nationally. If we find this why are the DNOs and yes some are taking horrific decisions. And in some cases charging. I’ve issued a safety alert for the Railway where I work. 

be good to gauge folks thoughts as a broken pen gives you CNE consideration in a home, not allowed by BS 7671 and also brings up the whole what is safe isolation with this in mind. We never consider earth as a energised conductor and only ever consider rise of voltage. Maybe with changing and ageing networks, non linear loads etc. We need to change the way we see things.

I live in hope the networks will be more open on this.

thoughts..

Parents
  • Hi Paul,

    This matter is something which concerns me, in respect of connecting coaxial cables to equipment installed within a domestic environment, to Class 1 (earthed chassis) devices such as amateur radio transmitters.

    The grounded coax is then taken outside, and often connected to a grounded antenna, where a PEN fault could give rise to shock to the installer, during installation, to the user whilst connecting the cable to his equipment, or could result in high fault current in the coax, with possible fire risk.

    I have prototyped a system which I am currently using, which introduces two high impedance points within the coaxial cable, ensuring the cable itself is not earthed to 50Hz, but does have a low impedance to ground for RF.

    Not being qualified in Part P, I would appreciate comments on the validity of this approach and whether it would be acceptable to the present Code. If not, what should I further consider?

    A rough outline of my thinking is available at www.bedsroad.org/.../earth_isolation_system_proposal_v3.pdf

    Many thanks in anticipation,

    Graham 

Reply
  • Hi Paul,

    This matter is something which concerns me, in respect of connecting coaxial cables to equipment installed within a domestic environment, to Class 1 (earthed chassis) devices such as amateur radio transmitters.

    The grounded coax is then taken outside, and often connected to a grounded antenna, where a PEN fault could give rise to shock to the installer, during installation, to the user whilst connecting the cable to his equipment, or could result in high fault current in the coax, with possible fire risk.

    I have prototyped a system which I am currently using, which introduces two high impedance points within the coaxial cable, ensuring the cable itself is not earthed to 50Hz, but does have a low impedance to ground for RF.

    Not being qualified in Part P, I would appreciate comments on the validity of this approach and whether it would be acceptable to the present Code. If not, what should I further consider?

    A rough outline of my thinking is available at www.bedsroad.org/.../earth_isolation_system_proposal_v3.pdf

    Many thanks in anticipation,

    Graham 