So for the past 5 years if so I have been seeing and experienced a phenomena known as diverted neutral current or diverted networks current.

It has a few names. Much like the incredibly slow realisation that type AC RCDs have had their day. Even though type A has been about over twenty years.

I get at least two / three messages a week from electricians who are now using clamp meters to check the earth conductors of LV installations. Low and behold they find anything from 2A up to 169A in a few cases.

I have research this at work for the last few years and some of the work I have ensured is published via the following link.

http://tangle-tamers.com/page21.html

We have also managed to produce a visual guide for measuring this issue. This work also helped with the Broken PEN IET article. 

It appears the aged life expired state of the LV network is a bigger problem and will only continue to grow. The use of CNE cable has been a tad o IMO. Years ago the RECs admitted cost was the key factor, but made the decision based upon a REC. a government owned network. Since privatisation the DNOs have fixed on fail, leaving the LV side unmonitored to a large extent. This is now slowly changing. But we assume a broken PEN conductor or failure of this can cause hazardous over voltages but also large amounts of network currents bypassing the broken PEN and importing and exporting on domestic earthing in some cases.

whilst the number are small in the scheme or things. It’s a growing issue. The network know about it. But the industry appears to not be discussing it. Why do we not get a safety alert for all electricians nationally. If we find this why are the DNOs and yes some are taking horrific decisions. And in some cases charging. I’ve issued a safety alert for the Railway where I work. 

be good to gauge folks thoughts as a broken pen gives you CNE consideration in a home, not allowed by BS 7671 and also brings up the whole what is safe isolation with this in mind. We never consider earth as a energised conductor and only ever consider rise of voltage. Maybe with changing and ageing networks, non linear loads etc. We need to change the way we see things.

I live in hope the networks will be more open on this.

thoughts..

Parents
  • Sorry if it reads as a great dump of random thoughts - it is sometimes the way I work. Happy to PM if you like. And here is that lost neutral detector redrawn for the 2020s. Sadly I no longer have a tame contact in ZA so I have no easy way of knowing if the idea has died a death or gone mainstream - but there is no obvious reference to it any more in anything I can find on the web so I am assuming the problem has probably been solved another way. Subtleties like company cut-outs, metering and so on are omitted..

    Mike

  • Regarding situations caused by broken, deteriorated, or in the case of South Africa, stolen, PEN conductors ...

    South Africa and Australia have looked at options using smart meter data from single-phase properties. Basically, voltage is monitored by the meters, and the distributor alerted if certain thresholds are met.

    If the distribution main is single-phase only, this method is almost fool-proof, but also on unbalanced mains, three-phase and single-phase meter data can also be used ... less foolproof and gives some false positives.

    I understand Australia have mandated their largest distributors to monitor for MEN faults in this way going forwards.

    A trick we appear to have missed in the UK going forwards, particularly as this fault is due to failure of component parts of the distribution network itself.

Reply
  • Regarding situations caused by broken, deteriorated, or in the case of South Africa, stolen, PEN conductors ...

    South Africa and Australia have looked at options using smart meter data from single-phase properties. Basically, voltage is monitored by the meters, and the distributor alerted if certain thresholds are met.

    If the distribution main is single-phase only, this method is almost fool-proof, but also on unbalanced mains, three-phase and single-phase meter data can also be used ... less foolproof and gives some false positives.

    I understand Australia have mandated their largest distributors to monitor for MEN faults in this way going forwards.

    A trick we appear to have missed in the UK going forwards, particularly as this fault is due to failure of component parts of the distribution network itself.