RCBO Working Temperature
We have had several reports from our engineers noting RCBOs protecting lighting circuits running at a significantly higher temperature than the rest of the DB or amibient.
One example from today from is a lighting RCBO running at 43 degrees where the ambiet temperature in the riser is 20 degrees.
The engineer has opened the DB up and there is nothing obviously wrong and all terminals are tight.
We've noticed the same thing several times recently and it always seems to be lighting circuits.
  • Modern RCBOs do have some electronics in them so do consume a bit constantly, even when unloaded.
    The wylex ones for example  take about 2.5mA from 230V (though with a capacitive power factor so not even half a watt. ) .  Obviously the MCB part dissipates a bit in normal use in proportion to the square of the load current, but no more than any other breaker (edit I have just loaded one up on the bench and at 5A  it drops 180mV, so ~ 35 milliohms and ~ 1 watt  )
    I'm at a loss to say why lighting should be much worse than anything else, unless they are much closer to full load or at the top of the box where it is hottest.
  • It's strange isn't it.  We're seeing it more and more on thermal surveys.  In todays example the board and RCBO are newish (less than 2 years old) and the circuit is LED lighting, nowhere near enough for it to be anywhere close to full load.
    I'm wondering if this potentially a faulty device given such an extreme variance in temperature from ambient.
  • and the circuit is LED lighting,
    This might be part of the problem. The led lights are not a pure resistive load and therefore there may be harmonics messing up the heating effects. Just a thought.....
  • The power factor of LED lamps can vary from adequate to terrible.  So don't assume the current draw bears any resemblance to the rated wattage.
  • I found this very informative.
    www.youtube.com/watch