Barriers to EV uptake - network reinforcement

Former Community Member
Former Community Member

Hello everyone. 

I'm going to be looking into barriers to Electric vehicle uptake over the next two months.

I found this report from BEAMA very interesting - https://www.beama.org.uk/resourceLibrary/growing-the-supply-chain.html

Without a lot of investment the prospect of Electric Vehicles not being changed, heat pumps not having sufficient power, or renewable generation not connecting are real possibilities, it says.

Rapid growth in local and distribution lines and cables is required. An additional 300,000 km of distribution cable is needed, along with 10% to 30% growth in substation numbers. Demand-side flexibility helps to mitigate this growth.

DNOs will need to invest a huge amount. Perhaps as much as £7bn/year, averaged over the next 15 years, and as much as £15bn/year 8 subsequently. 

For domestic technologies (including heat pumps and hybrid systems, resistive heating, heat storage systems, electric vehicle charging, domestic solar power and domestic electricity storage), the required investment between 2020 and 2050 is estimated to total circa £80bn. In contrast, the required investment in electricity distribution infrastructure12 is projected to total circa £330bn11 between 2020 and 2050. 

BEAMA says substantial acceleration in investment in the price control period 2028-2033 is necessary. Planning for this period must start now; delivery affects the whole supply chain, from DNOs to component providers, and adequate scaling up of manufacturing and installation may take years, it adds.

BEAMA also notes the skills shortage is a pressing concern, and one which must be addressed to step up supply chain activity.

If anyone is interested in talking to me about this or anything related to EVs, please drop me a line.

 

Conor McGlone

Investigative Journalist 

Engineering & Technology magazine 

 www.eandtmagazine.com 

 

Tel: 0207 344 5492/ 07725498128

Twitter: @ConorMcG1one

Parents
  • As far as I can tell based on SSE round here, the DNO is busy enough maintaining what it has on a 'fire brigade' basis (sometimes quite literally fire brigade actually), with not much slack for anything that looks like planning ahead for supplying all  3 phases to each house and fatter street cables generally.  The infrastructure is dated, most of it more than half a century old, and some sections are pre-war, and is certainly already creaking a bit at the current level of 5 to 10 amps per house average.

    It is worth looking at a typical DNOs ADMD figures for new housing, which are around the 2kw per house mark, and realize these numbers, used to size substations, street cabling and the 11 and 33kV distribution behind it, are  quite a bit more generous than previous versions used to size the network we currently have in many places.  If too many houses suddenly become a 30A load, or for that matter a  generator in sunny weather, the whole thing is way out of balance relative to the original cable sizing assumptions.

    Most of the DNOs publish their LV network design rules and loading assumptions on the web, some require an email sign up, but they may be worth a quick read to calibrate expectations - 70 houses each phase with a 100A cut out may well share a couple of  400A fuses per phase at a 500kVA substation for example.

    The BEAMA report is interesting but light on detail, and I do not believe for a moment that earth mats at substations will be the dominant future cost (figure 7) - if that was it we could start driving steel scaff poles instead. I think street cables and house supplies will dominate, and I am surprised they are not mentioned. Maybe the last leg of the LV network is not sexy enough for BEAMA to consider. (but without it the lights go out ! )

    Mike.

Reply
  • As far as I can tell based on SSE round here, the DNO is busy enough maintaining what it has on a 'fire brigade' basis (sometimes quite literally fire brigade actually), with not much slack for anything that looks like planning ahead for supplying all  3 phases to each house and fatter street cables generally.  The infrastructure is dated, most of it more than half a century old, and some sections are pre-war, and is certainly already creaking a bit at the current level of 5 to 10 amps per house average.

    It is worth looking at a typical DNOs ADMD figures for new housing, which are around the 2kw per house mark, and realize these numbers, used to size substations, street cabling and the 11 and 33kV distribution behind it, are  quite a bit more generous than previous versions used to size the network we currently have in many places.  If too many houses suddenly become a 30A load, or for that matter a  generator in sunny weather, the whole thing is way out of balance relative to the original cable sizing assumptions.

    Most of the DNOs publish their LV network design rules and loading assumptions on the web, some require an email sign up, but they may be worth a quick read to calibrate expectations - 70 houses each phase with a 100A cut out may well share a couple of  400A fuses per phase at a 500kVA substation for example.

    The BEAMA report is interesting but light on detail, and I do not believe for a moment that earth mats at substations will be the dominant future cost (figure 7) - if that was it we could start driving steel scaff poles instead. I think street cables and house supplies will dominate, and I am surprised they are not mentioned. Maybe the last leg of the LV network is not sexy enough for BEAMA to consider. (but without it the lights go out ! )

    Mike.