COP is a measure of efficiency a ratio of  Output energy/Input energy.  Thus if 2 kW electric input can give 4 kW of energy output then the COP=2

Google this:-   Can coefficient of performance be less than 1?  Google answer is

"Thus, we can say that the COP of the refrigerator and air-conditioner can be less than one or greater than one. The above formula also shows that the COP of the heat pump can never be less than one; it is always more than one."

I am not sure this final statement is correct because if you are driving the fridge compressor outside the heated room then all the friction power is lost into the atmosphere and not into the refrigerant.  So  if the heat source is more than say 10 degree.C less than the room temperature inside you could be loosing energy rather than saving it?

Parents
  • Has anyone out there a swimming pool ASHP as I would like them to do a little experiment for me as follows:-

    1. Take the temperature of the input pool water Tin

    2.Take the temperature of the water coming out of the ASHP Tout

    3. Take the temperature of the air entering the ASHP Tair

    4. Monitor the input voltage and current to the ASHP and average power used for a one hour period.=kWh input

    5. Measure the flow rate in litres per minute and multiply by 60 to get an hour rate and volume in litres/hr.

    6. Calculate the exact amount of energy produced per hour  by multiplying litres/hr times temperature difference Tout - Tin times 4.18 cal/Watt

    7 Calculate COP kWh output/kWh input.

    8 Repeat process with different air temperatureTair.  Say on warm day 20deg.C, average day15 deg.C, cool day10 deg.C and cold day 5 deg.C

    ( Graph the result COP against Air temperature Tair and let everyone see the results please.

Reply
  • Has anyone out there a swimming pool ASHP as I would like them to do a little experiment for me as follows:-

    1. Take the temperature of the input pool water Tin

    2.Take the temperature of the water coming out of the ASHP Tout

    3. Take the temperature of the air entering the ASHP Tair

    4. Monitor the input voltage and current to the ASHP and average power used for a one hour period.=kWh input

    5. Measure the flow rate in litres per minute and multiply by 60 to get an hour rate and volume in litres/hr.

    6. Calculate the exact amount of energy produced per hour  by multiplying litres/hr times temperature difference Tout - Tin times 4.18 cal/Watt

    7 Calculate COP kWh output/kWh input.

    8 Repeat process with different air temperatureTair.  Say on warm day 20deg.C, average day15 deg.C, cool day10 deg.C and cold day 5 deg.C

    ( Graph the result COP against Air temperature Tair and let everyone see the results please.