Designing data center installations involving multiple transformers and generators.
IEC60364 and BS7671 give ampacities for multiple trefoils but not quads
IMO, quads must have a lower ampacity than that given for trefoils spaced 2De on cable ladders
I note multicore 3 core and 4 core (and 5 core including earth) have the same ampacity
For singles, ONLY 3 cables are listed as trefoils with no mention of quads
What is the recommended solution for unbalanced parallel 3 phase 4 wire circuits with 100% neutral and smaller earths.
For example 6(4*240)/3*120G XLPE on cable ladder at 40C ambient