I want to canvass LED luminaire manufacturers to the problem that their PIR-controlled LED flood-lights might not be illuminating building exteriors correctly, but instead could lead to unsafe and unlit areas. I am referring to manufacturers’ totally sealing PIR-controlled LED flood-lights with no access to its internal PIR switched-live. Let me explain, as follows:
Traditionally, as an electrical engineer, I have always specified areas where multiple security flood-lights are required to be cabled with 3core & earth cable, where the additional core is used as a PIR switched-live to bring on all flood-lights together in a group. This is only possible if the PIR switched-live is accessible outside the flood-light, which of course it is on traditional halogen luminaires, but not on LED luminaires, which only have a 3core flex with no way to open the luminaire.
Of course, there are other alternatives, such as separate PIRs but additional cost implications make this option expensive, particularly on long pathways around the perimeter of large buildings. Also, multiple exit doors would result in multiple separate PIRs with yet more expense.
Simply, if manufacturers brought out a 4core flex, (live, neutral, earth & PIR switched-live, it gives electricians both options of each flood-light illuminating separately ignoring the additional PIR switched-live or bringing them all on together by connecting all grouped PIR switched-lives together. Whenever a single PIR triggers, it puts a live feed onto the additional core, which in turn puts a live feed onto the additional core bringing on all flood-lights connected to it.