Can anyone explain, in layman terms, how a mechanical and electrical interlock works between a generator switch, main switch and bus couplar on an LV Switchboard compared to just a mechanical interlock.
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
A pure mechanical interlock will only have moving parts between the switches so it is impossible to have them set in a dangerous position - in this case presumably you cannot set the generator and the mains on at the same time. An electro-mechanical interlock achieves the same end but at some point has wires and a solenoid or similar so an electrical signal from one switch is jamming or un-jamming the other. The electrical bit allows things to be further apart and gives greater freedom of orientation etc. However it does need an additional power supply and what happens if that supply fails needs to be carefully considered to fail-safe.
If you have more detail of the set-up it may be possible to be a bit less fuzzy.
Mike