Cable abandonment
When we abandon power cables (both LV and HV) we usually bag the field end and tie down the switchboard end to earth in the switchroom using cable abandonment kit. I was wondering if there's any Standard that require us to this.
Also, I would like to know the safety  implication of not  doing it.
  • To the best of my knowledge there's nothing in BS 7671 for LV installations.
    I suspect that it's one of these things that might be better one way in one set of circumstances and a different way in another - e.g. using a substation Earth might risk exporting nasty voltages during fault conditions - which might carry some risks. So might be better being left to engineering judgement.
  • would like to know the safety  implication of not  doing it.
    If the cable is left live and then has a 'bottle'  end (like half of a joint but cable comes in and not out again... ) then  it needs to be on all the maps as live and avoided while digging. However, at the end of a street where there is a sporting chance of extra houses being built later or something it is sometimes the right thing to do.
    Just leaving the cable floating leaves it open to accidental re- energisation, so something has to be done at the source end, and this allows it to be re-activated, even if only to inject a  tracing signal  if that is ever required, while cutting it short does not.
    Earthing it is normally the best option - a fully insulated cable does not really export the earth, and an old lead covered one just gives the place an extra electrode...
    It is pretty much essential to earth dead cores that run alongside live ones for any great part of the route, as capacitive coupling means that a 'floating' wire actually floats up to a voltage that can be dangerous to anyone who later touches it. For the same reason when one half of a pylon is turned off to be climbed, the 'off' side is not just isolated but also earthed.
  • Thanks for your contribution Andy
  • Thanks for your contribution Mike. I have  always seen this done for electrical abandoned cables in offshore Oil & Gas platforms. So, I was wondering if there's any Standard that recommended that practice. And just like Andy also mention, there should be some engineering judgement too.
  • There can be specific standards for different Hazardous area, for example BS EN 60079-14  is about Electrical apparatus for
    explosive gas atmospheres, and it does mention in multiple places that unused cores can either be "adequately insulated" or "connected to earth".
    The safety implications for the above is cables or cores having induced/unwanted potential that are able to create a spark in a zoned area that could be an ignition source.
    There may be more relevant standards used for offshore platforms.
  • Among the template observations that I have stored, the following statement is an example:Unused cables require disconnecting from the fuse way(s) and removing completely or connecting down to earth at both beginning and end of circuit (where they are exposed conductors not enclosed in an item of electrical equipment or insulated which may give rise to a shock due to induced current). Regulation 131.2.1
  • Thanks AMK. But it seems what we have in 7671 2018 edition is different as shown below:
  • I believe this regulation addresses the scenario where there are loose cables with exposed copper, which could create a potential difference and a hazard due to induced voltage, so direct contact.