Harmonics prediction on an installation with variable speed drives.

I have been asked by a client to provide a harmonics prediction report on an installation with variable speed drives. I have never done one or been required to look into this before. Could someone assist me with the sort of information i would need.

We are installing around 15 Variable speed drives that will control numerous pumps and agitators around the process plant.  It is a brand new facility, so at the moment I don't know the nature of the supply to the facility although i will be able to find this out soon.

The variable speed drives will range from 0.37kW and 5.5kW, 3 Phase so nothing big.

I basically need to know what sort of information I would need to obtain from the client and the VSD manufacturer, and then how I would compile that information into a report.

I assume i will need to provide a report on each drive rather than an overall report for the installation.

Any help will be greatly appreciated.

Parents
  • Hi Gareth,

    Given what you have said about the sizes of the VSD, I think an overall report for the installation would probably be the most use for the client and is probably what they need.

    From the client you need to know the existing supply details and other load details.  You may be able to gain the existing load details through some load monitoring if the site is operational.

    From the VSD supplier you need to gather information relating to harmonic currents at the operating point of the drives.  If you do not know the operating point or manufaccturer data isn't available for the particular operating point that you have then you can either work with the data that they do provide and adjust, or use the planning limit values from the EREC document, or take measurements from the drives

  • Thanks Chris that is extremely helpful.