HV Safety - Legislation on underrated HV Switchgear - 6.6kV Switchgear on 11kV Network

Hi,

I have come across HV switchgear in a recent audit that is underrated for the supply voltage. The switchgear is on a UK 11kV network, the switchgear itself is 11kV rated, as is one of the five outgoing circuit breakers. However, four of the five circuit breakers are 6.6kV rated. I am reporting these findings (along with others) and I am struggling to demonstrate the lack of compliance of this switchgear. I argue that using 6.6kV switchgear in an 11kV network is a breach in law but I can't back it with specific legislation. I can find guidance from the HSE on "overstressed" switchgear but I don't think this is really applicable (that's switchgear underrated for current fault levels, right?). I'd like to back up my statements in my report with some HSE guidance or H&S law but I am struggling.

Does anyone know of any specific legislation covering underrated HV switchgear/circuit breakers?

For more information, this switchgear is circa 1950s, oil filled and DMO (dependent manually operated).

Thanks,

Tony

Parents
  • Answers already provided point to legislation. However, IEC 60071-1 covers insulation coordination. For altitude below 1000 metres, switchgear should comply with these values. So check that the 6.6kV switchgear is not somehow really 11kV switchgear. The nameplate of datasheet will show the BIL and power frequency withstand ratings.

Reply
  • Answers already provided point to legislation. However, IEC 60071-1 covers insulation coordination. For altitude below 1000 metres, switchgear should comply with these values. So check that the 6.6kV switchgear is not somehow really 11kV switchgear. The nameplate of datasheet will show the BIL and power frequency withstand ratings.

Children
No Data