Non-IS cable routed through a Zone 0 hazardous area

Is it permissible to run a non-intrinsically safe (non-IS) armoured cable through a Zone 0 hazardous area on a UK offshore oil and gas platform? Please note that the cable is fed from a safe area (in the switchroom) and terminates on a 3-phase 415VAC motor in another safe area. Therefore, the cable is not terminated on any equipment in Zone 0; it merely passes through Zone 0 as a route. I need a reference from a standard or code to determine if this is acceptable.

I have attached relevant sections from IEC 60079-14 below:

 

Thanks for your help.

Parents
  • I dont know of any area in 60079 where it states what you want. 

    The only mention I know of exactly what you want to see, is in what is known as 'the blue book' , "Design, construction, modification, maintenance and decommissioning of filling stations" which is a standard for filling stations (fuel pumps and the like). Where it states the below,

    That standard does use a mix of 7671 & 60079, so I wouldn't rely on it for your purposes.

    You could make a case for it being allowed, providing the cable is suitable/ resistant to all the hazards present and doesnt have an ability to transfer the zone, that the connections are not in zone so it isn't a cable system for zone 0.

    Alternatively, is there a way for it to not be in zone, through rerouting, or containing that section?

    Sorry to have not been much help.

    Mike.

Reply
  • I dont know of any area in 60079 where it states what you want. 

    The only mention I know of exactly what you want to see, is in what is known as 'the blue book' , "Design, construction, modification, maintenance and decommissioning of filling stations" which is a standard for filling stations (fuel pumps and the like). Where it states the below,

    That standard does use a mix of 7671 & 60079, so I wouldn't rely on it for your purposes.

    You could make a case for it being allowed, providing the cable is suitable/ resistant to all the hazards present and doesnt have an ability to transfer the zone, that the connections are not in zone so it isn't a cable system for zone 0.

    Alternatively, is there a way for it to not be in zone, through rerouting, or containing that section?

    Sorry to have not been much help.

    Mike.

Children
  • Thank you so much for your support on this.

    Yes, rerouting is possible but will be very expensive due to its impact on production. The cable is an XLPE/SWA type, and there is no damage to the insulation, so we don’t expect gas from Zone 0 to become trapped and transfer to the termination points in the safe area. However, it is difficult to find a standard or code to support my argument.

    I will try to get hold of the code you referenced and review it.