Unbelievably I can't see a discussion thread on this already.
Anyone actually believing that a single transformer/substation fire shuts fully down one of the largest airports in the world?
Mod edit: including a link for context
Hello Sergio:
Just for the record I watch (live feed) the planes arriving and departing every morning from Heathrow Airport using youtube.
With the 5 hour spread between Florida and the UK it is usually about Noon UK time.
Hello Sergio:
Just adding to my earlier comment- Based on the live view, the air around Heathrow Airport appears to be highly contaminated.
Peter Brooks
Not sure what happened at Heathrow but for sure the emergency lights worked and presumably the control tower standby generator but security devises in passport control and computers were probably run off the airports mains power circuits which were not backed up with emergency generation.
Same with the baggage handling equipment. Hopefully, Heathrow have by now installed these critical areas with standby plant as it certainly should not cost as much as £20 million.
Have a look in this thread for one of my previous post with attachment where I simply put
Worth a read
The cost to the Heathrow reputation is 10 times more than the stated financial cost of £20m. It is also worth looking at who were the decision makers and who has just sold off a large share of Heathrow airport from their portfolio.
Final report published today https://www.neso.energy/document/363891/download
Thanks Chris.
An interesting read (with some lessons in the detail) although sadly at the highest level does sound like the common "opportunities were missed" maintenance failure.
"Using forensic analysis from both National Grid Electricity Transmission and London Fire
Brigade, this review has seen evidence that a catastrophic failure on one of SGT3’s high
voltage bushings caused a fire to ignite on the supergrid transformer. This was most likely
caused by moisture entering the bushing causing a short circuit. The electricity likely then
‘arced’ (causing sparks) which combined with air and heat to ignite the oil, resulting in a fire.
2.4 An elevated moisture reading in one of SGT3’s bushings had been detected in oil samples
taken in July 2018. According to National Grid Electricity Transmission’s relevant guidance, such
readings indicate ‘an imminent fault and that the bushing should be replaced’. While the
reading was recorded in National Grid Electricity Transmission’s online system, the mitigations
appropriate to its severity were not actioned."
So that is the nature of the network fault, but, and it is quite a big but, why, given Heathrow has 3 in-feeds, could they not switch over to the other 2 and keep going - clearly that is what National Grid expected would happen as they did not consider the transformer bushing a priority - and presumably would have had to power some kit off to change it anyway.
If you mean the airport, with three infeeds, I'd say by the read of it they could (and did within 6-7 hours from memory) but it required manual intervention. Probably this was in part due to SSEN enforcing open points to ensure that their feeders aren't paralleled through the customer's network (usually this means transferrable key interlocks etc).
If you mean the Hyde 66kV SS, the first SGT tripped and the substation did indeed recover using the third SGT which was provided as a running reserve. But the fire caused the second SGT to trip a little bit later either due to fire damage to its control kiosk or exploding bushings, and the third SGT was taken out automatically by the control scheme as it wasn't designed to operate solo.
Still does not explain why Heathrow internal network relied on manual switching to re-configure their network.Most
large hospitals have automatic reconfiguration of their own network in event of a fault.
And sufficient on site generation to run the whole hospital.
Surely Heathrow should have the same on their site??