Unbelievably I can't see a discussion thread on this already.
Anyone actually believing that a single transformer/substation fire shuts fully down one of the largest airports in the world?
Mod edit: including a link for context
"Of course, it's quite possible that they did understand the risks entirely, but decided that it wasn't worth the extra cost of implementing any mitigation as they calculated that they wouldn't bear the brunt of the costs of any outage."
This was my thoughts - Further up the chain i had refernced that an article suggested the outage cost Heathrow Airport £20m. The cost for the private network reconfiguration, additional generators, UPSs etc could easiliy run to multiples of this given the airport virtually never shuts. I could see that someone may have thought why bother with all the disruption and compensation to airlines/retailers etc when if the 'black swan' event happened they could opportunistically and necessarily reconfigure the network and it would all be someone else's fault.
Heathrow Airport's arguement here would be that the 'black swan' event was not actually a black swan event and was readily known about by National Grid.
I'm not sure anyone in a room full of engineers would have predcted one of the transformer would fail in such spectacular fashion and take out two other supplies at the same time.
Heathrow may have assumed that two separate supplies to substation A was sufficient redundancy, that those two incoming supplies should have sufficient independence such that they should not both fail at once.
I'm not sure I could be convinced of that logic - even if the supply to the substation was multiply redundant, the cable from the substation to the airport would still provide a single point of failure. I can't see how anyone can reasonably treat any single grid supply as 100% reliable - if it hadn't happened for this reason, it could well have happened for a dozen other perfectly justifiable reasons. They had multiple supplies, but didn't seem capable of utilizing them within a reasonable timescale (i.e. co-ordinated with UPS run times for critical equipment).
There are two cables from the North Hyde substation to the airport - the incident report shows that Heathrow Substation A was supplied by two separate circuits, fed separately at 66kV from the North Hyde substation with each circuit having its own 66kV/33kV step-down transformer, providing two separate 33kV supplies into Substation A - see Single Line Diagram on page 13, Figure 3.
Therefore a single cable fault, or other fault, on one circuit would not be expected to interrupt all supplies to substation A.
Further, the North Hyde 66kV substation had 5 separate 66kV incoming supplies - 3 x 275kV/66kV Supergrid transformers and 2 x 66kV interconnectors to/from Iver.
Given the 5 separate supplies into North Hyde, on the face of it, it doesn't seem unreasonable to assume at least one of the circuits supplying Substation A would remain energised, or if it did fail would be restored within a short time frame. As it was, the report timeline shows it took ~10 hours to re-energise the 66kV substation.
At least one engineer knew - the one who assessed the fire risk, identifying that with the lack of physical separation, a fire on one transformer was at risk of causing damage or the fire to spread to the adjacent one, taking them both out of service, and so went to the efforts of getting a deluge fire protection system added to protect them both.
There's plenty of hindsight bias to go around;-)