I am currently working on a project involving a DC charger rated for a 1500VDC, 3200A switchboard. We have a type-tested switchboard rated for a 100kA/1s main busbar, with a peak withstand of 220kA at 690VAC. The new switchboard, which should be rated for 1500VDC, 3200A, also requires a 100kA/1s DC busbar.
My question is: Can we still use the same busbar that has already been tested for AC circuits? For now, let's set aside dielectric strength and focus solely on short-circuit withstand strength.
this is a clause from Clause – IEC 61439 2020 - 10.11.5.4
‘’ An AC short-time current test may be used to verify a rated DC short-time withstand current and a rated DC peak
withstand current providing the test with AC has a peak current equal to the rated DC peak withstand current and
the RMS value of the short-time current is at least equal to the rated DC short-time withstand current. When
substituting a DC test by an AC test, it should be recognized that the thermal and dynamic stresses of the AC test are
higher than those of the equivalent DC test. ‘’
If the AC short-circuit withstand test is more rigorous than the DC test, my understanding is that we can use the same busbar for the DC application as long as we maintain the same clearances and design parameters as the AC-tested switchboard. Is this correct?