Single pole and switched neutral vs DP for EV

Hi All

Would a single module, single pole and switched neutral RCBO satisfy 722.531.3.1 disconnecting all live conductors?

Usually we fit 40A Type A DP RCBOs but at other installations I'm coming across these single SP+N RCBOs installed for domestic chargers.

Thanks in advance 

Dan

Parents
  • Usually we fit 40A Type A DP RCBOs but at other installations I'm coming across these single SP+N RCBOs installed for domestic chargers.

    The key difference with a true 2-pole RCBO is that the mcb function (overcurrent detection) is present for both poles, whereas with this device, the RCD function works for both poles (the sense coil is around L and N poles), but there is no mcb (overcurrent) function on the neutral pole, although it will disconnect the neutral for an overcurrent on the line pole.

    The picture you posted is a unidirectional device, so it can't be used for V2G functionality.

    With any switch or protective device with a neutral pole, especially three-phase, regardless of whether it is just switched, there may be a difference in the rated making and  breaking current of the neutral pole, as in three-phase it can be mechanically linked to make first and break last.

Reply
  • Usually we fit 40A Type A DP RCBOs but at other installations I'm coming across these single SP+N RCBOs installed for domestic chargers.

    The key difference with a true 2-pole RCBO is that the mcb function (overcurrent detection) is present for both poles, whereas with this device, the RCD function works for both poles (the sense coil is around L and N poles), but there is no mcb (overcurrent) function on the neutral pole, although it will disconnect the neutral for an overcurrent on the line pole.

    The picture you posted is a unidirectional device, so it can't be used for V2G functionality.

    With any switch or protective device with a neutral pole, especially three-phase, regardless of whether it is just switched, there may be a difference in the rated making and  breaking current of the neutral pole, as in three-phase it can be mechanically linked to make first and break last.