Why is my RCD tripping when doing a Zs test and the tester is on no trip
R1+R2 was 0.59
RCD tests all ok
Why is my RCD tripping when doing a Zs test and the tester is on no trip
R1+R2 was 0.59
RCD tests all ok
The Megger MFT uses a 15 mA loop test current, so a little leakage in the circuit, and connected loads will cause a trip, as will a having RCD that trips around 15 mA..
A lot of RCDs wI’ll trip around 17 mA, so it doesn’t need much standing leakage in the installation for the RCD to trip whilst loop testing.
The Megger MFT uses a 15 mA loop test current, so a little leakage in the circuit, and connected loads will cause a trip, as will a having RCD that trips around 15 mA..
A lot of RCDs wI’ll trip around 17 mA, so it doesn’t need much standing leakage in the installation for the RCD to trip whilst loop testing.