I suspect you're not going to get a nice yes/no answer for this - as there's no clear definition of what makes such a system safe or unsafe in the first place.
As a bit of background there was a thread about the way open-pen devices like this work - Open PEN detection for 722.411.4.1 (iv) - as you seen there are situations where the results are perhaps less than ideal anyway. Increasing the acceptable voltage range will increasing the probability of the system remaining connected in a hazardous situation, but given the original system is not entirely perfect in the first place, whether that constitutes a significant reduction in safety is debatable rather than calculable.
I could see an argument that if the device had some additional mechanism for reducing the risk from shock under broken PEN conditions - not just voltage measuring, but say monitoring the c.p.c. current and disconnecting immediately if hazardous shock levels were present (say >10mA), and as that wasn't compromised at all by the voltage limit change, the overall risk might not be significantly increased.
- Andy.
Thank you very much for this Andy - and I would agree with you that there is no simple yes or no answer here. I am in a difficult posistion due to the fact we have manufacturers stating that voltages can be increased while myself as the installer is left scrambling to understand the comlexities of this decision.
I really feel at a lost at present, the charger I am discussing does have additional monitoring on the CPC so that is a benefit, I am still unsure how I can justify that in terms of upping the voltages - against what is in BS7671? Would you have any thought or comment on that?
Thank you very much for this Andy - and I would agree with you that there is no simple yes or no answer here. I am in a difficult posistion due to the fact we have manufacturers stating that voltages can be increased while myself as the installer is left scrambling to understand the comlexities of this decision.
I really feel at a lost at present, the charger I am discussing does have additional monitoring on the CPC so that is a benefit, I am still unsure how I can justify that in terms of upping the voltages - against what is in BS7671? Would you have any thought or comment on that?
I see that in New Zealand the have changed their supply voltage limits because of Prosumer issues from +6% to +10%, while keeping the DNO supply level at +6% to allow for back feeding from solar on longer distribution lines.
see https://www.youtube.com/watch?v=s8RXQERPzMY "The newly announced NZ Grid Voltage Increase explained".
This may give one view on how to explain things, even if it's not directly equivalent.
The other option is to distinguish between a "Fault" and "Disturbance" (aka Dangerous vs Annoying).
Thank you very much Philip, I will have a look at that video.
Hello Philip:
The video was excellent but highlighted a fact I had forgotten about the delivery of electrical power to New Zealand and the UK.
It mentioned that houses are only supplied with single phase power.
Here in the US houses are supplied with split phase power with the two phases being 180 degrees apart giving 110-120 volts and 240 volts. The later being used for electric ovens, heat pumps and driers.
Peter Brooks
Palm Bay FL
True, though I tend now to think of the US supplies as 220V centre tapped :wink:
Hello Philip:-
In my old house the 110 and 240 volt supplies are treated differently.
The 110 is routed to sockets using Al wires while the 240 is routed using copper wires to heavy duty sockets .
Today (1st of August) hurricane supplies are TAX free. This includes small motor/generator sets, used in the event of loss of electrical power.
My memory (as I don't own one ) is that they only have single phase 110 volt output.. Now I will have to go to my big box hardware store to look at them.
Also there are bigger units, which I assume have both output voltages.
Peter Brooks
Palm Bay