PV Importing Not Decreasing as expected
Im an electrical supervisor at a manufacturing plant. We installed a 1MW PV system to our roof, which has been a good success in generating power.
But we noticed through the year, as weather is improving during summer our generation increase, but our imported power from the grid tends to remaim the same. We were expecting the imported power to fall as the generated power increases.
Nothing has changed at the plant. Yes, product tonnage various but not much. Our energy KPI are being affected.
We have checked our 7 PV inverters metering against our utility class calibrated Fluke 1777 power quality analyser, and all 7 are accurate.
Our factory power set up is as follows. We receive x2 11kV feeds from the grid which is ran around our x3 switchrooms (11kV ring main). Out of the x3 switchroom, we have x7 11kV to 400V transformers, and through one of these LV boards our PV system is connected to.
Is there anything we are missing here? As i said we generating good amounts of electricity, so from Janurary commissioning to August we've generated around 900MW of power.
  • Hi Aron,
    Without looking at the data it could be a number of things but the first question to ask is whether there's a mismatch between the load profile and the generation. E.g. You might have a uniform consumption pattern while the solar peaks at midday; while the total GWh might be the same, so net zero, you'll be importing mornings and evenings and exporting at midday.
    Could also be sub-half-hourly metering fluctations (perhaps you have a very intermittent load), grid curtailment / ANM, metering or HV network setup, performance issues and a few other things.
    I will send you a PM.
    Jam
  • Hi Jam,
    We altered our electricity supply network to absorb more PV generation by adding more loading. So we dont export.
    Aron.
  • As in you moved the NOP so all three substations (or at least the larger load centres) are fed through the same incomer as the PV?
    For the avoidance of confusion, when you say "imported power tends to remain the same" are we talking instantaneous or peak import power (kW), or import energy (kWh) and if the latter over what timescales are you taking measurements (HH, daily etc)? Apologies if it's an obvious question, but they're often mistaken and it'll save chasing the wrong ideas.
    Is the 1MW PV system 1MWp of PV with say 7x100kW inverters? Is there a G100 export limitation scheme, ANM or other DNO control of the generation? Is the PV generating as expected (do you have meters on the generation or can you interrogate the inverters)? Are there any other generators parallel with the grid (e.g. CHP)?
    For comparison, what was the peak and average daytime demand (kW) before the PV was installed? What's the load profile like: Is your plant a 24/7 continuous operation or are your processes cyclic or irregular depending on what's being produced?
    Presumably your load power factor is reasonably close to unity.
  • Yea, correct we moved the NOP so that x2 switchrooms is absorbing the PV generation.
    The PV are not fed through the grid incomer.
    Imported energy (kWh) stays the same. We do have access to H-H data but dont tend to use it really.
    Yes, correct its a 1MWp!
    The meters are reading correctly because we connected our utility grade power quality analyser (Fluke 1777). Results were accurate.
    No other generators in parallel with grid that i am aware of.
    Plant is 24/7 and has a relatively constant loading. Weekends might dip a bit.
    Our PF is close to unity aswell.
  • Additionally, we take monthly meter readings of the x2 incomers. And have access to H-H data. But we tend to use the monthly kWh reading in the energy supplier invoice to calculate various things such as KPIs
  • I have to ask...
    If you have two separate 11kV feeds from the grid, has someone managed to set it up so that all the big loads are on one feed, while the export is on the other?
    1MWp will only deliver 1MW if it's a sunny day and the sun is directly over the panels.  Not necessarily midday GMT; it will depend on which way the panels are pointing.
    If it's cloudy, expect a lot less.  At the wrong time of day, you will also get less.
    If your usage is so high that you never export, then maybe the generation is so small you don't notice it when aggregated on daily basis.
  • We were exporting (which we didnt want this to happen) so we moved the 11kV 'normal open point' so that x2 out of 3 of our switchroom were now absorbing the PV generation rather than 1 before. Afterwards, we stopped exporting. So we sorted that issue out. We were expecting for the imported kWh to decrease as PV increased (kWh) throughout the year. But its not the case. Same loading.
  • If you're only looking at monthly data and your load is 24/7 then my first suggestion is to look at the half-hourly data and look for it there. It's quite likely that you'll see a depression in import figures during the day correlated to the generation.
    If it's a constant load most of it will not be offset by the PV: As Simon says you will (depending on the DC/AC ratio) only get the full effect when it's bright enough, so at least 50% of the time (night) your import will be as before. Furthermore the PV array will only generate up to the inverter AC rating, not the array DC (kWp) rating.
    Conversely you may be spilling excess into the grid still if your constant load is less than the installed generator capacity.
  • In terms of diagnosing the cause of the problem, I doubt monthly metering volumes will be much help because they don't provide the granularity necessary to see what's going on.
    I would start with the half-hourly metered volumes - your boundary/supplier half-hourly metering for both the import and the export across the boundary, combined with whatever hourly, half-hourly, or minute level data is available from your solar system.
    With those data sets, it should then be possible to put the three data-sets together, dip-check a few days and visualise what is going on during a typical working day, to see where the energy is going.