Hi everyone,
I am faced with a technical problem related to the synchronization of diesel generators.
My customer had 2 gensets that are operating in parallel to provide emergency power source to the financial institute installations.
Recently, a third unit of genset was added and the design was to have all these 3 units to be supplying power to a common genset supply switchboard which the gensets shall be synchronized.
G1 and G1 (genset 1 & 2) are the 2 existing units, and they could sync up well.
With the new G3 unit added, site test was done to test the synchronization. G3 could close it supply breaker to the common bus with either of the older units (G1 or G2). When a dummy load test was initiated, the G3 will get its earth fault relay to be activated. No tripping will occur when G3 and G1 are sync-up and running at no load condition. This is similar when G3 and G2 are sync-up and running at no-load condition.
Earth fault relay activates when the dummy load (3 wire system resistive load bank) was activated. Despite increasing the setting of the Earth fault protection for G3 to 20% of the rated output, the EF relay still had picked up.
What shall be checked for such case?
a. Common Neutral-earth grounding? (only single point connection of the Neutral common bus to the earth?)
b. Does the G3 genset configuration (controls / parameter settings) plays a part for such nuisance tripping?