Guidance on Long-Run DC Cable Design for Lighting
Hi all,
I’m designing a greenhouse lighting system with a centralized DC PSU feeding multiple luminaires. The DC voltage varies between 200 V and 500 V.
The distance from the centralized panel to the first luminaire is around 50 m, and the total circuit length is approximately 100 m.
I have experience with AC cable calculations and design, but this is my first time working with long-run DC cabling. I would greatly appreciate expert guidance on:
  • Any special considerations when selecting cables or performing cable calculations for DC circuits — what is different from AC design?
  • Relevant standards or documents I should refer to.
  • Use of overload and RCD protection: do I need a specific type of RCD for DC circuits (Type B / RDC-PD), especially since I must provide minimum 300 mA RCD protection for greenhouse lighting?
I’m trying to expand my experience into DCcable design, so any advice or pointers would be greatly appreciated.
Thanks in advance for your support!
    Not really. AC calculations are done on the basis of "r.m.s." values - i.e. the d.c. equivalent - so Ohms Law and related resistance based calculations should be just the same. (For larger cables inductive/reactive effects will be rather different of course, but for smaller cables typically only the resistive component is considered anyway).
    If it's in the UK or simialr, BS 7671 would be a good starting point I would have thought.
    This bit is tricker. Fuses and MCBs should properly be d.c. rated, as breaking d.c. arcs is much more difficult than for the equivalent a.c. situation. RCDs I suspect will be very problematic - I don't know of any available ones that work on a d.c. supply. B-type ones for instance are usually good for spotting d.c. residual currents, but sill need an a.c. supply as far as I know.
  • Thank you very much for your support.
    Yes, this project is based in the UK.
    Regarding RCD protection : do you think it would be advisable to install an RCD upstream of the AC/DC converter (i.e., the power supply unit)? I don’t want to create any issues by doing so, but I’d like to confirm whether such an RCD would actually be effective in detecting and protecting against leakage currents on the DC side of the circuit.
    Again, I greatly appreciate your support.
  •  do you think it would be advisable to install an RCD upstream of the AC/DC converter (i.e., the power supply unit)?
    Depends on how the unit works internally and how the d.c. side is referenced to Earth (or not), but if it's the usual design where the DC side is separated from the AC side then the RCD will likely provide no benefit at all, as faults on the d.c. side won't result in a L-N imbalance on the a.c. side.
    You might want to take a step back here - 500V d.c. is a pretty unusual system (and there might be good reasons for that). Have a think about how to provide shock protection - ADS is only one option of several and might be fairly awkward to achieve (e.g. for 500V you'd need max 0.1s disconnection time and without RCDs you'd conventionally have to rely on overcurrent protective devices - and so to achieve 0.1s you'll require very substantial prospective fault currents - which in turn may be difficult to guarantee from a PSU arrangement unless it's massively oversized and you'll likely need pretty thick cables too to keep the loop impedances down).
    I guess there's more to this project than meets the eye - presumably there's some reason for preferring d.c. over conventional 230/400V a.c. systems. SELV/PELV is more conventional for d.c. systems - but extra low voltages tend to have much more onerous voltage drops so are likely to be impractical for circuit lengths of many tens let alone hundreds of metres. Double/reinforced insulation might be a better bet, but does need some extra care and on-going supervision (which may or may not be suitable for the situation you have in mind). If you are sticking with ADS, lowing the voltage a little might help - 400V or below and you can have a 0.4s disconnection time, and 1s for 230V or below - which should make things rather easier. If you can arrange the supply to be centre-tap earthed - e.g. so it's 115-0-115 rather than 0-230 you can have the same voltage available for the loads, but half the voltage available for shocks (to Earth) (below 120V you don't have to disconnect at all).
  • Normally higher voltage DC systems would either have dedicated fault detection - either being fully floating and looking for leakage to earth much like an insulation monitor in an IT system, or by having a clear ground to one side or the other, and then wired in earthed conduit or armoured cable,
    As above this all depends how the DC is derived, and leakage detection is likley to be engineered in or not at all. Be aware that DC is also nastier in terms of corrosion in any environment that is not completely dry if there is steady earth leakage. The word 'greenhouse' rather suggests water and random bits of earthed metal.
    The reason for AC is not just that we can use transformers and smaller light switches, the corrosion thing is also a consideration.
  • One wonders about the idea of "hall effect DC Current transformers" which are available through the usual channels [i.e the cheap hobby stuff, in particular].
    It appears to me that the usual current difference between the go-return wires and a suitable 'soft iron'  style core could be suitable (no steel armouring ;-).
    It may be that the residual current, as a magnetic field strength is a bit low for the direct Hall effect, but then one would shift to 'Flux Gate' sensing (used in phones to measure the earth's magnetic file for the Compass facility) might be the way to sense DC.
    The problem here is that it become a functional safety issue requiring sufficient reliability, predictability and analysis rather than a Heath Robinson [Rube Goldberg] lash-up.
  • Thank you very much for your insights
  • Actually correct operation / fault detection is done with hall effect current sensing in certain systems - thinking the DC HT supplies for transmitters and RF generators  and so on  where a direct current sense would be awkward for reasons of isolation . Designing for unconditionally fail-safe operation is quite an involved process however, as each system is essentially bespoke. The exact level at which to set trip limits is also a thorny topic.
  • Might be worth noting that for a similar - but different - scenario with DC circuits and elevated voltage and limited fault current, namely PV installations, the solution is to work on the basis of using the protection method of double or reinforced insulation, because ADS is so difficult to reliably achieve. This does of course bring its own problems (uninformed persons expecting the Supply to be Automatically Disconnected in the event of a fault being a significant one). There are cables and equipment marketed specifically to that application.
    In the UK, most PV installations are arranged IT with insulation monitoring. However, some systems, more so in other jurisdictions, are earthed on one pole with fault detection achieved by monitoring current in the earth connection (something like a DC MCB or fuse with auxiliary contact causing the main circuit to trip, or an earth fault relay, depending on the fault level and disconnection requirements). This is likely to be quicker than an IMD and easier to physically measure than a traditional residual (differential) earth fault detection, but may not meet your requirements for an agricultural facility. You also need galvanic isolation to ensure that the earth fault currents can't escape around your earth link via the AC system.
    Who specified the DC voltage? Assuming that they think it normal for a greenhouse, perhaps they can provide more guidance?
    Also, a significant gotcha that I don't think has been mentioned yet: The cable specification might be relatively straightforward but do make sure all your switchgear, connectors (etc) are rated for the appropriate DC application. Don't assume it'll be fine... it probably won't. Most of the time DC will derate the equipment, and a lot of switchgear isn't even tested/rated for DC.
  • Hi Jam,
    Thank you for your support.
    After all the comments by everyone I am about to ask the PSU supplier to incoperate ADS with IMD for the system.
    About the DC voltage, this is the operating voltage of lights. it wont be 500V all the time but 200V-500V (vary with dimming condition).