Main Protective Bonding for Heat Pump Pipe works
  • In our ASHP installations, the flow and return pipework runs above ground externally before entering the building. The heat pump is earthed via a CPC from the switch board, and the pipework is connected to the unit. As the external pipework is not buried and does not appear to be in contact with earth, we are assessing whether it constitutes an extraneous-conductive-part. Could anyone confirm if main protective bonding is required at the point of entry in line with BS 7671 Regulation 544.1.2?
  • For our GSHP installations, the borehole pipework is plastic and remains non-metallic from the ground up. There is approximately 1.2 m of metal pipework externally above ground before entering the building and connecting to the system. As the external metal section is connected to plastic pipework and not in contact with earth, we believe it does not introduce earth potential and therefore would not be considered an extraneous-conductive-part. The GSHP unit is earthed via a CPC from the switch board. Can you confirm that in this case, main protective bonding is not required in accordance with BS 7671 Regulation 544.1.2?
  • In a plantroom, where metal heating/chilled water pipework is installed entirely within the building and connected to heat pumps, and the heat pumps are earthed via a CPC, is main protective bonding required in this case?
  • Hard to be 100% sure without seeing it, but from what you describe the parts don't sound like they would be extraneous-conductive-parts that would require main bonding (they may still be extraneous-conductive-part w.r.t. some location though - e.g. if they were to run through a bathroom - so might require supplementary bonding for that location unless exemptions apply). Things to double check for would be things like metallic pipe supports - especially if on a significant support (e.g. unistrut) which could pick up a potential from a damp external masonry wall or the ground, or if internal pipework were buried in damp masonry work (unlikely for new work, but far from unknown in old installations).
  • I also presume the HP itself is isolated from the ground - e.g. by rubber mounting feet,
  • Are there touch distances involved?  Sounds very like to car charger open PEN style discussions where you just can't win...
  • Don't go there!
    Arguably a HP is more like a lamp post, one of those green comms cabinets by the side of the road, the metallic flue poking out of the wall from a gas boiler or a class I outside light - unlike a car door handle, people grab hold of such things relatively rarely, so the risks (from broken PENs) are lower. On the other side of the coin HPs can have significant protective conductor currents - so maintaining a solid c.p.c. connection is probably more important than usual - so something like an open-PEN device with moving contacts on the c.p.c. might well reduce a small risk but increase another one.