I'm working on a resilience study for a large industrial facility supplied from a grid substation shared with the local distribution network. The study follows process disruptions attributed to voltage dips originating on the supply side and propagating into the plant's internal network.
I'd like to invite the forum's experience on assessment approach.
The Problem:
Power quality monitoring at the point of common coupling has confirmed recurring voltage dips, propagating through step-down transformers into the plant network and causing undervoltage-related trips on large motors and variable-speed drives, along with associated production disruption. The plant has no local generation and is fully dependent on the grid connection.
Assessment Approach:
I'm modelling the network from the point of common coupling down to the plant's internal distribution level, to characterise dip propagation and assess vulnerability at each load point. This includes calibrating fault conditions to replicate recorded dip behaviour, representing dynamic motor loads for drives known to trip during these events, and running sensitivity cases across the recorded event envelope.
A key outstanding item is the grid fault strength and impedance angle at the point of common coupling, currently being pursued through the utility.
What I'm Seeking:
- What modelling approach has given the most reliable correlation with measured plant behaviour, particularly for motor dynamics and drive representation?
- How have others handled the grid equivalent at the point of common coupling when utility fault-level data is unavailable or uncertain?
- Is there value in assessing harmonic performance alongside dip propagation for a plant of this nature, or is that generally treated as a separate exercise?
- Where the utility grid is the source and the plant has no control over it, what contractual or regulatory mechanisms have others used to engage the utility on power quality obligations?
Broader Question:
This looks like a systemic issue for facilities drawing from shared substations serving mixed industrial and distribution loads. Is there published guidance specifically addressing voltage dip assessment methodology for large grid-connected industrial plants, beyond standard equipment immunity testing references?
Grateful for any experience or critique of the approach above.