Hi All, we have been asked to install tails from a new DNO 400A TPN cut-out to an existing panelboard. This new DNO supply appears to be TN-S (we are trying to source the quotation to confirm the DNO supply arrangement.) The building is of steel frame cons

1No. PME and 1No. TN-S supply into a single steel frame building.

Parents
  • The DNO is obliged to give you the information under R.28 of ESQCR 2002:

    A distributor shall provide, in respect of any existing or proposed consumer’s installation which is connected or is to be connected to his network, to any person who can show a reasonable cause for requiring the information, a written statement of—

    ...

    (d) the type of earthing system applicable to the connection;

Reply
  • The DNO is obliged to give you the information under R.28 of ESQCR 2002:

    A distributor shall provide, in respect of any existing or proposed consumer’s installation which is connected or is to be connected to his network, to any person who can show a reasonable cause for requiring the information, a written statement of—

    ...

    (d) the type of earthing system applicable to the connection;

Children