This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

How to wire up a consumer unit

A semi-detached house has a prehistoric fuse box with rewirable ceramic fuses. It will shortly be replaced with a modern consumer unit. The existing circuits are:



 



1. Lights



2. Upstairs sockets



3. Downstairs sockets



4. Kitchen sockets



5. Cooker



6. Shower



 



The following circuits will be added to the consumer unit:



 



7. Central heating



8. Burglar alarm and CCTV



9. Outside lights



 



I have been informed that the best choice is a split load consumer unit with two RCDs and space for RCBOs. My intention is that circuit 8 has its own RCBO but what is the optimal way to allocate circuits to RCD A and RCD B? Also, should any other circuits have their own RCBO?


Parents
  • If you don't mind paying for it, the best option would be to lose the RCDs entirely, and put everything on RCBOs.  But that would be more expensive.


    The two RCD solution is a bit of a compromise, but still perfectly OK for most homes.  It's really not that critical - just spread the load across the RCDs to avoid overloading them, and try to minimise the inconvenience if one trips.
Reply
  • If you don't mind paying for it, the best option would be to lose the RCDs entirely, and put everything on RCBOs.  But that would be more expensive.


    The two RCD solution is a bit of a compromise, but still perfectly OK for most homes.  It's really not that critical - just spread the load across the RCDs to avoid overloading them, and try to minimise the inconvenience if one trips.
Children
No Data