Main switch short circuit capacity.

Some guidance please.

Three phase TN-S supply from a private 800 kVA transformer. Distribution via a 240mm2 4 core SWA approx 20m in length from a transformer mounted feed pillar and protected by 315A fuses. At the intake position 100A BS 1361 type II fuses are fitted. I was looking to install a REC 4 main switch down stream from which would be three phase distribution by 10kA rated MCB's. My question is about the suitability of the main switch and its short circuit capacity at it's point of installation with regard to prospective fault current at this point which will be greater than 16kA or do the BS 1361 afford adequate protection for the switch ? Your thoughts please.
Parents
  • Thanks Mike for a very informative description for what is a complex subject. My values are simply calculated using the IET Electrical Installation design guide to give me a general idea as to what I'm dealing with. I think as you stated, it falls with manufacturer being able to confirm one way or the other.

    As a matter of interest and looking BS7671 Characteristics for the fuse, that for a 0.1 disconnection time that the fault clears at 1450 A which I take it is true up to 33kA. It's just the switch being able to with stand the energy let through during this period.


    Many thanks again.
Reply
  • Thanks Mike for a very informative description for what is a complex subject. My values are simply calculated using the IET Electrical Installation design guide to give me a general idea as to what I'm dealing with. I think as you stated, it falls with manufacturer being able to confirm one way or the other.

    As a matter of interest and looking BS7671 Characteristics for the fuse, that for a 0.1 disconnection time that the fault clears at 1450 A which I take it is true up to 33kA. It's just the switch being able to with stand the energy let through during this period.


    Many thanks again.