Former Community Member
Former Community Member
Hi all, any comments welcome on this one.
Is it still acceptable to have a socket outlet for a specific use not rcd protected under the 18th?
I fitted a single 13a socket outlet recently in a loft space for one of my regular customers, it is to supply a security camera system and the suppliers asked for a socket to be provided. It is supplied from the first floor lighting circuit which doesn't have rcd protection. (16th. ed. board) There is not the slightest chance of the socket being used to supply anything else and I would like to issue a mwc stating that the socket is only to be used for this specific purpose. If it's a major issue I could get back to the customer and arrange to fit an rcbo but I don't really think that is necessary? Thinking now about going back to change socket for an rcd protected one?
Parents

  • Nowhere do the regs say you can't have a socket on a lighting circuit



    Indeed - if fact regulation 559.5.1 (v) says explicitly that it's permitted - and indeed commonly done in some areas where the ability to unplug an individual luminaire etc. for servicing etc is useful.


      - Andy.
Reply

  • Nowhere do the regs say you can't have a socket on a lighting circuit



    Indeed - if fact regulation 559.5.1 (v) says explicitly that it's permitted - and indeed commonly done in some areas where the ability to unplug an individual luminaire etc. for servicing etc is useful.


      - Andy.