Paul Skyrme:
My opinion here will deviate from what is stated in BS 7671, and, for some crazy reason that there has been no explanation of the product standard for RCD socket outlets (and fused connection units) have been removed from BS 7671:2018, so that could require a deviation, me, I'd not worry and fit one, including a deviation if necessary.
The requirement in BS 7671:2018 is that ALL socket outlets in domestic premises must be RCD protected.
SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.
Paul Skyrme:
My opinion here will deviate from what is stated in BS 7671, and, for some crazy reason that there has been no explanation of the product standard for RCD socket outlets (and fused connection units) have been removed from BS 7671:2018, so that could require a deviation, me, I'd not worry and fit one, including a deviation if necessary.