gkenyon:
Paul Skyrme:
My opinion here will deviate from what is stated in BS 7671, and, for some crazy reason that there has been no explanation of the product standard for RCD socket outlets (and fused connection units) have been removed from BS 7671:2018, so that could require a deviation, me, I'd not worry and fit one, including a deviation if necessary.
The requirement in BS 7671:2018 is that ALL socket outlets in domestic premises must be RCD protected.The current version of BS 7288 actually says that additional protection should already be in place within the installation. The last sentence of the first paragraph of Clause 1 of BS 7288:2016 states:
SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.
gkenyon:
Paul Skyrme:
My opinion here will deviate from what is stated in BS 7671, and, for some crazy reason that there has been no explanation of the product standard for RCD socket outlets (and fused connection units) have been removed from BS 7671:2018, so that could require a deviation, me, I'd not worry and fit one, including a deviation if necessary.
The requirement in BS 7671:2018 is that ALL socket outlets in domestic premises must be RCD protected.The current version of BS 7288 actually says that additional protection should already be in place within the installation. The last sentence of the first paragraph of Clause 1 of BS 7288:2016 states:
SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.