18th question.

Former Community Member
Former Community Member
Hi all, any comments welcome on this one.
Is it still acceptable to have a socket outlet for a specific use not rcd protected under the 18th?
I fitted a single 13a socket outlet recently in a loft space for one of my regular customers, it is to supply a security camera system and the suppliers asked for a socket to be provided. It is supplied from the first floor lighting circuit which doesn't have rcd protection. (16th. ed. board) There is not the slightest chance of the socket being used to supply anything else and I would like to issue a mwc stating that the socket is only to be used for this specific purpose. If it's a major issue I could get back to the customer and arrange to fit an rcbo but I don't really think that is necessary? Thinking now about going back to change socket for an rcd protected one?
Parents

  • Sparkingchip:

    The problem is that some LED lighting, such as patio lights that can be installed in timber decking and the like can be installed in kitchen plinths and the like, but they are supplied with a plug in LED driver or transformer.


    So you need a 13-amp socket to plug the lights into the lighting circuit hidden away under the kitchen cabinets or elsewhere as you cannot cut the plug off and hard wire them.


    Similar issues occur with CCTV equipment and the like, it can easily run off a lighting circuit, but needs a plug to plug the mains adapter into.


    Andy B.




    But the moving goal post requires all domestic lighting circuits and cables in walls to be RCD, introducing more what ifs.


    Andy B. 

Reply

  • Sparkingchip:

    The problem is that some LED lighting, such as patio lights that can be installed in timber decking and the like can be installed in kitchen plinths and the like, but they are supplied with a plug in LED driver or transformer.


    So you need a 13-amp socket to plug the lights into the lighting circuit hidden away under the kitchen cabinets or elsewhere as you cannot cut the plug off and hard wire them.


    Similar issues occur with CCTV equipment and the like, it can easily run off a lighting circuit, but needs a plug to plug the mains adapter into.


    Andy B.




    But the moving goal post requires all domestic lighting circuits and cables in walls to be RCD, introducing more what ifs.


    Andy B. 