Effectiveness is deemed to have been verified where an RCD meeting the requirements of Regulation 415.1.1
disconnects within 40 ms when tested at a current equal to or higher than five times its rated residual operating
current.
well, to only do a 5 times test meets the letter of the regs. which I think is not really an adequate standard for a case like this, especially considering what is being protected.
However, additional testing above the bare minimum reveals that it is clearly not working right after all, and really needs changing soon.
In your shoes I might do a a few more tests to see what level it does trip at - if it fires OK at 35mA , it is less of an immediate risk than if it still does not fire at 120mA.
So assuming it does not pass close enough to 30mA that it could be tolerances on the test meter accuracy, then ..
Report may have listed no failures against BS7671, if you had only done the minimum requred tests, but you tested more thoroughly
and noted that the RCD protecting the bathroom is not operating as it should and needs replacement.
.....a sheltered housing flat.
Wet room for disabled occupant.