SWA Cable Above ground and earthing the armour

When using SWA cable underground I always earth the armour, regardless of whether the armour is used as the cpc or not. The armour does provide some mechanical protection and it is important that the armour is earthed so that if the cable were penetrated (e.g. by a garden fork), the supply would automatically be disconnected by the protective device under this fault condition.
I have a situation on an existing domestic installation where I will be changing the consumer unit.  The 3-core SWA cable to the hot-tub rotary isolator is above ground and clipped to an outside wall.
The cable has not been terminated with brass glands, and at the ends the armour have been taped up, so no exposed conductive parts. The armour is not being used as the cpc.
At the rotary isolator for the hot-tub, stuffing glands have been used. The cable feeding the hot-tub does rest on the ground for about 1m before going into the hot-tub enclosure.
The earthing arrangement is TNCS, however at the hot-tub rotary isolator, the TNCS earth is not exported and there is an earth electrode for  the hot-tub’s cpc
Would you expect the armour to be earthed? Is it acceptable to terminate SWA without brass glands?
Parents
  • I agree Geoff, and normally I would earth it at source with appropriate gland. But seeing this relatively  new installation made me ask the question. I think it is pretty rough, but can’t come up with any regulations it does not comply with.


    That said, this document from Prysmian https://www.whyprysmian.co.uk/BS5467.pdf makes the following statement on page 2;  “Armour bonded and earthed at both ends -  Yes”. That looks like a manufacturer’s instruction/recommendation to me.

Reply
  • I agree Geoff, and normally I would earth it at source with appropriate gland. But seeing this relatively  new installation made me ask the question. I think it is pretty rough, but can’t come up with any regulations it does not comply with.


    That said, this document from Prysmian https://www.whyprysmian.co.uk/BS5467.pdf makes the following statement on page 2;  “Armour bonded and earthed at both ends -  Yes”. That looks like a manufacturer’s instruction/recommendation to me.