SWA Cable Above ground and earthing the armour

When using SWA cable underground I always earth the armour, regardless of whether the armour is used as the cpc or not. The armour does provide some mechanical protection and it is important that the armour is earthed so that if the cable were penetrated (e.g. by a garden fork), the supply would automatically be disconnected by the protective device under this fault condition.
I have a situation on an existing domestic installation where I will be changing the consumer unit.  The 3-core SWA cable to the hot-tub rotary isolator is above ground and clipped to an outside wall.
The cable has not been terminated with brass glands, and at the ends the armour have been taped up, so no exposed conductive parts. The armour is not being used as the cpc.
At the rotary isolator for the hot-tub, stuffing glands have been used. The cable feeding the hot-tub does rest on the ground for about 1m before going into the hot-tub enclosure.
The earthing arrangement is TNCS, however at the hot-tub rotary isolator, the TNCS earth is not exported and there is an earth electrode for  the hot-tub’s cpc
Would you expect the armour to be earthed? Is it acceptable to terminate SWA without brass glands?
Parents
  • My view is that the one metre length of S.W.A running on the ground would persuade me to correctly gland the S.W.A. cable at the supply end with a correctly fitted gland and I would earth the gland at the supply end. This will protect the cable live conductors and ensure correct disconnection in case of cable damage. As the armouring is protecting the live conductors it must be earthed. 131.2.2., 134.1.1., The use of R.C.D.s is not recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in Sections 411 to 414. (415.1.2)


    Z.
Reply
  • My view is that the one metre length of S.W.A running on the ground would persuade me to correctly gland the S.W.A. cable at the supply end with a correctly fitted gland and I would earth the gland at the supply end. This will protect the cable live conductors and ensure correct disconnection in case of cable damage. As the armouring is protecting the live conductors it must be earthed. 131.2.2., 134.1.1., The use of R.C.D.s is not recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in Sections 411 to 414. (415.1.2)


    Z.