I assume that there is insufficient armour to be able to attach it to a brass gland at the new CU. It is appropriate to terminate the armouring in a stuffing gland at the downstream end, but I cannot find a regulation which requires a surface-mounted SWA cable to be earthed at the upstream end.
The only caveat is that if the outer sheath were damaged, the armour would become an exposed conductive part.We are back to the discussion about the fact that SWA has single insulated conductors surrounded by a plastic filler or plastic yarn with wire wrapped around them covered with a plastic sheath.
Single insulated conductors inside metal containment, so the metal containment needs earthing just as metal trunking or conduit containing single insulated singles does.So what's the regulation, Andy?
I don't think that the armour of SWA can be considered to be exposed unless the cable has been damaged.So Chris, why use the S.W.A. at all? Would you just run twin and earth down to the load, even for the 1 metre section on the ground?
Z.
Zoomup:
Chris Pearson:
Sparkingchip:
Chris Pearson:
I assume that there is insufficient armour to be able to attach it to a brass gland at the new CU. It is appropriate to terminate the armouring in a stuffing gland at the downstream end, but I cannot find a regulation which requires a surface-mounted SWA cable to be earthed at the upstream end.
The only caveat is that if the outer sheath were damaged, the armour would become an exposed conductive part.We are back to the discussion about the fact that SWA has single insulated conductors surrounded by a plastic filler or plastic yarn with wire wrapped around them covered with a plastic sheath.
Single insulated conductors inside metal containment, so the metal containment needs earthing just as metal trunking or conduit containing single insulated singles does.So what's the regulation, Andy?
I don't think that the armour of SWA can be considered to be exposed unless the cable has been damaged.So Chris, why use the S.W.A. at all? Would you just run twin and earth down to the load, even for the 1 metre section on the ground?